RE: Debian Compatable UPS?

From: Seth Goodman (sethg_at_GoodmanAssociates.com)
Date: 09/20/05

  • Next message: Josh Battles: "Re: Debian Compatable UPS?"
    To: <debian-user@lists.debian.org>
    Date: Tue, 20 Sep 2005 12:56:30 -0500
    
    

    > From: John Hasler [mailto:jhasler@debian.org]
    > Sent: Tuesday, September 20, 2005 11:16 AM
    >
    >
    > Josh Battles writes:
    > > I would think that a marine deep cycle would be better suited to the
    > > task...
    >
    > Only if you expect to have a power failure every day. Deep cycle
    > batteries are designed to be deeply discharged with great frequency.
    > Car batteries are designed to frequently delivery large amounts of
    > current and be either on float charge or disconnected most of the time.
    > The ideal is a standby power battery, but car batteries are close enough
    > and readily available.

    John is right, there is a large difference in design of batteries for
    different applications. There are basically two physical cell types based
    on the form of electrolyte: flooded liquid cells and gel cells. Car and
    marine batteries have flooded liquid cells. These release hydrogen and
    water vapor when overcharged, though the newer ones ("no maintenance")
    manage to decrease the loss of water enough that the battery usually dies of
    other causes by the time that becomes a problem.

    Gel cells are designed to trap the hydrogen before it gets out, which they
    are mostly successful at. They can also be mounted in any position and lose
    very little water vapor with a properly designed charger. When originally
    introduced, we all thought gel cells would have incredibly long lifetimes,
    but that has turned out to be untrue. Their useful life is not very
    different from flooded liquid cells. None of the lead-acid constructions
    can deliver much of their stored charge at low temperatures and all are
    difficult to charge without damaging them at high temperatures.

    Both physical types of cell can be optimized for short high-rate discharges
    (typical UPS), long low-rate discharges (emergency lighting), very deep
    discharges (marine batteries) or other criteria. One problem for the
    consumer is that gel cells optimized for completely different applications
    still have the same external package size and nameplate rating. Thus, you
    can go to the battery store and get a 12V, 7Amp-hour battery and get any one
    of a number of constructions that may not function properly for a given
    application.

    Here are a few generalizations of my own, from having designed a lot of
    battery backup circuitry.

    - old-style car or marine batteries with removable cell caps are somewhat
    hazardous and are best suited for facilities that are set up to handle them
    (i.e. telecom offices, data centers)

    - newer "no maintenance" car batteries are still hazardous, though somewhat
    less than the older style

    - gel cells are very safe, but cost more for the same capacity compared to
    flooded liquid cells

    - pick a battery that is optimized for the operating condition you want;
    that is, do you want to run from batteries for ten minutes or two hours?
    it's not the same battery

    - if you greatly oversize the battery, you have more flexibility in what it
    will do, though you paid for it

    - pay attention to the design of the charging system; a good charging system
    will greatly extend (or at least not shorten) the useful life of the
    battery; poorly designed chargers can cause any battery to dry out and
    prematurely fail

    - battery chargers need to know the temperature of the _battery_ to properly
    terminate charging; that means don't keep the battery outside and the
    charger inside, unless the charger is a special design with a remote
    temperature sensor

    - recharge any disconnected lead-acid batteries every few months; they
    slowly self-discharge and need to be "topped off" periodically

    - never let a lead-acid battery sit around discharged, as it will gradually
    suffer a permanent loss of capacity

    --
    Seth Goodman
    -- 
    To UNSUBSCRIBE, email to debian-user-REQUEST@lists.debian.org 
    with a subject of "unsubscribe". Trouble? Contact listmaster@lists.debian.org
    

  • Next message: Josh Battles: "Re: Debian Compatable UPS?"

    Relevant Pages

    • Re: Cost per mile over 10 yr life?
      ... They aren't talking about "AA" size NiMH cells of course, ... If you stick a small Li-Ion battery pack in it, ... During ultra rapid charge the per cell voltage may necessarily need to be ... My particular area of expertise is in power electronics. ...
      (sci.energy)
    • Re: Circuit Design Q. - battery charger
      ... bright sunlight in perfectly clear weather. ... cells so you have sufficient voltage to charge the batteries? ... will be very unlikely you will give the battery much of an overcharge. ...
      (sci.electronics.design)
    • Re: Some quick questions about cells and batteries...
      ... Every battery chemistry requires its own unique ... manner of charging (and sensing when a charge is finished). ... reach a certain voltage, and then charged at constant voltage there-after. ... damaging the cells and/or creating a fire. ...
      (sci.electronics.basics)
    • Re: Source for LCD monitor? / PX-13 mercury cell substitute
      ... A WeinCell MRB625 battery is supposed to be a proper $4 substitute ... screws, removing the four cells, and relacing the tabs -- certainly ... The mention of the gold bonded diodes reminded me of my first ... selected transistor to make what was sold as a "ref-amp" (reference ...
      (rec.crafts.metalworking)
    • Re: Another Novice Q. - recharging - Volts and Amps
      ... To charge my 4 little 1.2V AA NiMH batteries, ... following solar cells ... "...the solar operating voltage must be higher than the battery voltage..." ...
      (sci.electronics.basics)

    Loading